ZERO sequence CURRENT in LG faultFor LG fault, all the sequence currents are equal.\({I_{R0}} = \FRAC{{{I_f}}}{3} = \frac{{300}}{3} = 100\;A\)WhereIR0 is the zero-sequence currentif is the fault currentType of faultPercentage of occurrenceZero sequence currentL-G70 – 80%Ia0 ≠ 0L-L15 – 20%Ia0 = 0L-L-G 10%Ia0 ≠ 0L-L-L<1%Ia0 = 0L-L-L-G2 – 3%Ia0 ≠ 0 The type of fault that includes ground has zero-sequence current.Like L-G, L-L-G, L-L-L-GImportance of Zero sequence current: In case of Ground faults like LG, LLG the fault current pass through the ground to the neutral and providing a relay between the neutral and ground, the zero sequence currents are passing through this relay for protection of electrical equipment like generator, transformer etc and the relay is called earth fault relay or ground fault relay. "> ZERO sequence CURRENT in LG faultFor LG fault, all the sequence currents are equal.\({I_{R0}} = \FRAC{{{I_f}}}{3} = \frac{{300}}{3} = 100\;A\)WhereIR0 is the zero-sequence currentif is the fault currentType of faultPercentage of occurrenceZero sequence currentL-G70 – 80%Ia0 ≠ 0L-L15 – 20%Ia0 = 0L-L-G 10%Ia0 ≠ 0L-L-L<1%Ia0 = 0L-L-L-G2 – 3%Ia0 ≠ 0 The type of fault that includes ground has zero-sequence current.Like L-G, L-L-G, L-L-L-GImportance of Zero sequence current: In case of Ground faults like LG, LLG the fault current pass through the ground to the neutral and providing a relay between the neutral and ground, the zero sequence currents are passing through this relay for protection of electrical equipment like generator, transformer etc and the relay is called earth fault relay or ground fault relay. ">

What will the zero-sequence current when line to ground fault occurs and the current in faulted phase is 300 A?

Current Affairs General Awareness in Current Affairs 8 months ago

  282   0   0   0   0 tuteeHUB earn credit +10 pts

5 Star Rating 1 Rating
ZERO sequence CURRENT in LG faultFor LG fault, all the sequence currents are equal.\({I_{R0}} = \FRAC{{{I_f}}}{3} = \frac{{300}}{3} = 100\;A\)WhereIR0 is the zero-sequence currentif is the fault currentType of faultPercentage of occurrenceZero sequence currentL-G70 – 80%Ia0 ≠ 0L-L15 – 20%Ia0 = 0L-L-G 10%Ia0 ≠ 0L-L-L<1%Ia0 = 0L-L-L-G2 – 3%Ia0 ≠ 0 The type of fault that includes ground has zero-sequence current.Like L-G, L-L-G, L-L-L-GImportance of Zero sequence current: In case of Ground faults like LG, LLG the fault current pass through the ground to the neutral and providing a relay between the neutral and ground, the zero sequence currents are passing through this relay for protection of electrical equipment like generator, transformer etc and the relay is called earth fault relay or ground fault relay.

Posted on 27 Oct 2024, this text provides information on Current Affairs related to General Awareness in Current Affairs. Please note that while accuracy is prioritized, the data presented might not be entirely correct or up-to-date. This information is offered for general knowledge and informational purposes only, and should not be considered as a substitute for professional advice.

Take Quiz To Earn Credits!

Turn Your Knowledge into Earnings.

tuteehub_quiz

Tuteehub forum answer Answers

Post Answer

No matter what stage you're at in your education or career, TuteeHub will help you reach the next level that you're aiming for. Simply,Choose a subject/topic and get started in self-paced practice sessions to improve your knowledge and scores.